Caddy Pyramid system

Status
Not open for further replies.

PCN

Senior Member
Location
New England
We are hoping to use the new Caddy Pyramid 300 equipment supports for several 4" pvc conduits installed on a membrane roof.

My question is, how in the world to ground this?

One seperate conduit just to carry an equipment ground and terminate to a mechanical lug at each support? We might have 30 of these critters.

Any thoughts would be appreciated.

http://www.erico.com/products/caddypyramid300.asp
 
Maybe I am not to bright but I have used many of these and never thought of bonding them.
 
I don't see those as likely to become energized. If they are you have a bigger issue with the pipe and insulation on the conductor.
 