ron said:I think the point is, that you can't install a fully rated fuse or circuit breaker that is listed below the calculated fault current. ...
Yes that would be true. Again, I don't see where this is news. I re-read my posts, I don't see where I ever suggested that. I certainly have tried to adamantly suggest that one must pay attention to: drum roll ....(there were three items - this is a test to see if you read the posts - without looking back - Name That Criteria!)
ron said:... The installation of a random current limiting fuse upstream does not reduce fault current for the underrated over current device ...
Wow. "Random" is an interesting word choice. I don't know how to answer that. I guess I never considered any equipment selection I made to be "random".
ron said:...when the lower rated device begins opening before the higher rated device. This can happen instantaneously, even before you can begin seeing it on a time current coordination curve characteristic curve. ...
This is an excellent example of claims that elude me. What I am hearing you say is one can't believe the mfg trip curves. That clearing times can happen much faster than is shown on the mfg curves. Just out of curousity, do you have any published test data that supports that claim?
ron said:...It must be a series rated tested combination if you wish to use one to protect the other in a fault condition.
Another interesting claim. My reading of 240.86(A) is certainly different. But you're in good company - that's my intrepretation of Jim's thinking.
"Random" selection of equipment ??. Ouch - That was a slap in the face.