I don't see either making a difference. There is no special consideration provided in Article 220 for an electric water heater of any type. At best, a water heater can qualify as one of the 4 appliances fastened in place under 220.53. But that is true regardless of type.when replacing a tank water heater in a dwelling unit with tankless do you calculate load for service same as you would water heater or insta hot.
Ditto!Welcome to the forum![]()
...i.e their branch circuit rating... and has no effect on service load calculation. :roll:According to 422.13, the continuous-load requirement only applies to storage-type (tank) water heaters.
...
Oh....i.e their branch circuit rating... and has no effect on service load calculation. :roll:
Yes.when replacing a tank water heater in a dwelling unit with tankless do you calculate load for service same as you would water heater or insta hot.