Weird situation: Normal 480V 3-Phase loads total 21.6A
In addition, there are (2) 25kVA 1-Phase transformers connected using different power legs (one of them shared, obviously.)
I get the 25kVA single phase each requires 25,000VA/480V = 52.1A
The issue is the leg that's shared between the two single phase transformers. I wouldn't expect them to double the current on the shared leg to 104.2A, but I also know it won't be the 52.1A alone added to the other 3-Phase loads. I was half inclined to treat the scenario as though there was 25kVA across each par of legs for a total of 75kVA and calculate it as a 3-Phase transformer for 75,000VA/(480*sqrt(3)) = 90.2A and add that to the 21.6A.
What say you?
In addition, there are (2) 25kVA 1-Phase transformers connected using different power legs (one of them shared, obviously.)
I get the 25kVA single phase each requires 25,000VA/480V = 52.1A
The issue is the leg that's shared between the two single phase transformers. I wouldn't expect them to double the current on the shared leg to 104.2A, but I also know it won't be the 52.1A alone added to the other 3-Phase loads. I was half inclined to treat the scenario as though there was 25kVA across each par of legs for a total of 75kVA and calculate it as a 3-Phase transformer for 75,000VA/(480*sqrt(3)) = 90.2A and add that to the 21.6A.
What say you?