Calculating 3-Phase current requirements where (2) 1-phase transformers are installed?

Tip DS

I'm here.
Location
The Great Meme State
Occupation
Electrical Engineer
Weird situation: Normal 480V 3-Phase loads total 21.6A
In addition, there are (2) 25kVA 1-Phase transformers connected using different power legs (one of them shared, obviously.)

I get the 25kVA single phase each requires 25,000VA/480V = 52.1A

The issue is the leg that's shared between the two single phase transformers. I wouldn't expect them to double the current on the shared leg to 104.2A, but I also know it won't be the 52.1A alone added to the other 3-Phase loads. I was half inclined to treat the scenario as though there was 25kVA across each par of legs for a total of 75kVA and calculate it as a 3-Phase transformer for 75,000VA/(480*sqrt(3)) = 90.2A and add that to the 21.6A.

What say you?
 
The issue is the leg that's shared between the two single phase transformers. I wouldn't expect them to double the current on the shared leg to 104.2A, but I also know it won't be the 52.1A alone added to the other 3-Phase loads.
If you assume that those two single phase transformers are seeing loads with comparable phase shifts between current and voltage (e.g. all loads resistive, so 0 phase shift), then the two currents you add in the shared leg are 60 degrees out of phase, so the sum has a magnitude of 52.1A * sqrt(3).

I was half inclined to treat the scenario as though there was 25kVA across each par of legs for a total of 75kVA and calculate it as a 3-Phase transformer for 75,000VA/(480*sqrt(3)) = 90.2A and add that to the 21.6A.
Indeed, that will give you the same result as above.

Cheers, Wayne
 
The issue is the leg that's shared between the two single phase transformers. I wouldn't expect them to double the current on the shared leg to 104.2A, but I also know it won't be the 52.1A alone added to the other 3-Phase loads. I was half inclined to treat the scenario as though there was 25kVA across each par of legs for a total of 75kVA and calculate it as a 3-Phase transformer for 75,000VA/(480*sqrt(3)) = 90.2A and add that to the 21.6A.

What say you?

That is the easiest way to get a good approximation.

The true answer will likely be lower since the 25kVA transformers are likely not fully loaded.

As @wwhitney describes, the currents on the shared leg are out of phase, so they don't simply add.
 
It looks like the OP is describing a 3-phase open delta configuration using equally sized transformers. For balanced 3-phase loading this will look like it was a 43.25kVA transfomer (.577x75).
 
It looks like the OP is describing a 3-phase open delta configuration using equally sized transformers.
I believe the OP is talking about sizing a feeder that supplies 21.6A of 3-phase loads and (the primary side of) two single phase transformers.

Cheers, Wayne
 