I am in the process of sizing a 3 phase 208/120v 4-W service for an existing site currently fed single phase. We will be back feeding existing feeders that are feeding the single phase motors and additional non-motor continuous load of 165A. I have the following loads:
Motor Loads:
(1) 3ph, 208v, 20hp = FLA 59.4a
(1) 1ph, 208v, 10hp = FLA 55a
(5) 1ph, 208v, 7.5hp = FLA 44a
(1) 1ph, 208v, 3hp = FLA 18.7a
(2) 1ph, 120v, 1 hp = FLA 8.8a
59.4 x 1.25 = 74.25 + 55 + (44x5) + 18.7 + (8.8x2) = 385.55A
Other continuous load of 165A
Total Connected Load: 550.55A (551A)
Minimum service size 600A?
Please look over my calculations and confirm they are correct or feel free to comment as to what is incorrect.
Thank you in advance.