When calculating the circuit ampacity for the feed to the primary of a transformer do you use the transformer primary rated current or do you have to use the transformer primary rated current + 125% to size conductors. I always thought it was just primary rated current.
So if I have primary 100kVA at 480V then transformer has primary rated current of 208A. When sizing conductor do I use 208, or must I use 208 * 1.25= 260A to determine ampacity for feeder?
Also when you have a transformer which you are including with other loads on a feeder circuit then do you use the transformer primary rating only added to other continuous loads and then apply 125% to the total continous load total only once?