23 apartments from a 1923 building are each served by one 30A 240V and one 20A 120V fused circuit. Each apartment's 240V circuit has a Water Heater 1500 W & Stovetop 840 W. Which has no problem with a 30A circuit.
However, the 120V circuit has an AC Unit 5.2A, Microwave 6.66A, Refrigerator 3.75A, and Receptacles/lighting calculation at 3VA/SQ of 11.51A. With multipliers it comes out to 28.4A total for the wire size.
This obviously exceeds the 20A rating of the #12 wire. So when I asked the customer about this she mentioned that they don't have any problems with blown fuses. My question is how do you do the load calculation on these units without making them run another circuit to each unit? Because of other code issues the county has come in and red tag any future electrical till a load cal has been done for everthing in the building.
However, the 120V circuit has an AC Unit 5.2A, Microwave 6.66A, Refrigerator 3.75A, and Receptacles/lighting calculation at 3VA/SQ of 11.51A. With multipliers it comes out to 28.4A total for the wire size.
This obviously exceeds the 20A rating of the #12 wire. So when I asked the customer about this she mentioned that they don't have any problems with blown fuses. My question is how do you do the load calculation on these units without making them run another circuit to each unit? Because of other code issues the county has come in and red tag any future electrical till a load cal has been done for everthing in the building.