Hi,
I'm currrently checking the lighting panel board schedules of pass projects and noticed a "minor error" in the calculation of the load current.
In it, the designer averaged the currents of the three phases (current phase "a" + current phase "b" + current of phase "c") and multiply this with the demand factor. What should have been done was to choose the HIGHEST phase current and multiply that with the demand factor.
I've tried looking at NEC for the exact article that directly talks about this but i couldn't find it. Can anyone give me leads, in NEC or other references, that directly addresses this issue?
Thanks,