I need help. I have a proposed total load of 88,270VA in my building. The load is non-continuous. The service will be 3Φ 208Y/120v. All breakers will be single pole and double pole (single phase loads only). If I balance my loads, what will be my amp load per phase? I just can't seem to figure out how to calculate service load in a 3 phase service. Is it as easy as 88,270VA/208/1.73 = 245A/Leg, and then size service based on that?
I just don't understand the 1.73 in the calculations. If a 3Φ service is loaded with single phase loads...it just gets confusing to me. Any clarity would be helpful.
Thanks!