I've been discussing panel schedules in our office. Currently when filling out the load for lighting, the panel schedule that is being used in the offices takes the lighting at a demand factor 125% (you enter the VA load of the light fixtures on a circuit and the schedule multiplies that value by 1.25 to calculate the total VA load on the panel). The two sections that are in question (2005 NEC) are 220.42 and 220.20(A).
Some of the group contended that because of 220.20(A) stating that continuous load is multiplied by 125% to calculate the size of overcurrent protection serving the circuit (and lighting being a continuous load) that the 125% also applied to the VA load entered into the panel schedule.
The other faction contended that, refering to paragraph and table 220.42, that the demand factor used should be 100% (office building application) and that the VA value entered on the on the panel schedule should only be multiplied by one.
Are there any other sections that apply to this question (we didn't note any others that applied directly to this question)? And what is the value that lighting load VA needs to be multiplied by to calculate the total VA load on a panel?
Thanks in advance,
Some of the group contended that because of 220.20(A) stating that continuous load is multiplied by 125% to calculate the size of overcurrent protection serving the circuit (and lighting being a continuous load) that the 125% also applied to the VA load entered into the panel schedule.
The other faction contended that, refering to paragraph and table 220.42, that the demand factor used should be 100% (office building application) and that the VA value entered on the on the panel schedule should only be multiplied by one.
Are there any other sections that apply to this question (we didn't note any others that applied directly to this question)? And what is the value that lighting load VA needs to be multiplied by to calculate the total VA load on a panel?
Thanks in advance,