Here is the proper way to calculate 3 phase loads.
1.) Office building 24000 square feet
2.) from table 220.12, 24000 x 3.5 = 84000VA
3.) 84000 x 1.25 = 105000 total lighting load after all demand factors
4.) 105000VA / system voltage 480Y/277
5.) 480Y x 1.732 = 831V for three phase systems
6.) 105000VA / 831V = 126A total amp load
Prove math below:
7.) 24, 20A circuits, 277V, 16A each
8.) 277V * 16A = 4432VA
9.) 4432VA * 24 circuits = 106368VA (105000VA)