single phase or three phase?I haven't gotten involved in anything else other than the main disconnect, 600 amps just seemed too little for 20 all electric units. With the chart 220.8 we see its actually 38% which pushes us to 612 amps. That would've been a huge and costly mistake to replace an entire main disconnect. I will find out where he got the 32% from and show him the chart.
Thanks everyone for the help will report back.
single phase or three phase?
I have a low income housing complex I have done work off and on at over the years, 600 amp 208/120 three phase, all electric, 20 units (spread out via 5 different buildings) plus the admin laundry and community center in an additional building. I never done an actual load calculation on the facility, but would be willing to bet you seldom if ever could come in and measure more then 400 amps on the main supply.
1965 give or take a year or two.It is actually single phase. How new/well insulated is the complex?