I was confused about this question:

In a 3-wire 220V circuit with a balanced load, what is the load of the neutral?

I usually picked 0V as my answer, but I think that is not correct? :happysad:

Some help in explaining this to me would be great. I got my exam coming up soon. Thanks.
 

Smart $

Esteemed Member
Location
Ohio
I was confused about this question:

In a 3-wire 220V circuit with a balanced load, what is the load of the neutral?

I usually picked 0V as my answer, but I think that is not correct? :happysad:

Some help in explaining this to me would be great. I got my exam coming up soon. Thanks.
It's a poorly worded question: 220V is not a standard voltage... 208V and 240V are; also a load does not exist on one wire (e.g. "load of the neutral").

Nevertheless, the desired answer is likely 0A (not 0V). The question leads me to assume this is a split single phase circuit, two line conductors, one neutral conductor, and states a balanced load... meaning no current on the neutral conductor.
 
Last edited:

fmtjfw

Senior Member
Yes, if in fact that's actually how the question was worded.

Since it is a balanced load, the voltage makes no difference, the neutral home run always carries 0A.

In providing the balance the non-home run parts of the neutral can carry anything up to the highest phase current.

Just being pedantic.:)
 

jumper

Senior Member
Since it is a balanced load, the voltage makes no difference, the neutral home run always carries 0A.

In providing the balance the non-home run parts of the neutral can carry anything up to the highest phase current.

Just being pedantic.:)

Er,,,, you might wanna check Besoeker"s profile before you lecture him. Senior Power EE with like 40 years experience.;)
 

Smart $

Esteemed Member
Location
Ohio
Since it is a balanced load, the voltage makes no difference, the neutral home run always carries 0A.

In providing the balance the non-home run parts of the neutral can carry anything up to the highest phase current.

Just being pedantic.:)
Er,,,, you might wanna check Besoeker"s profile before you lecture him. Senior Power EE with like 40 years experience.;)
Additionally, since standard voltage was not used, it could be similar to a 120/208V 3-wire circuit, where the rms neutral current magnitude is equal to the either line's magnitude.
 

Besoeker

Senior Member
Location
UK
Er,,,, you might wanna check Besoeker"s profile before you lecture him. Senior Power EE with like 40 years experience.;)
Ta mate!
Actually, that's something the English might say and I'm not English.
So I wouldn't........:)

Back to the topic.......
My simple point was that the way the OP stated the question might be based on memory.
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Still trying to understand. If I have A = 20A, B=20A, and C=0A, I get sqrt(400+400+0-400-0-0) = 20

Am I missing something (phase angles or harmonics)?
Well, if the OP is using slang 220 but means 230 or 240 it is single phase and your formula is for a wye. If it is in fact a wye, your formula is correct and as Dennis points out, with odd order harmonics the neutral can have more current than the two ungrounded conductors.

Roger
 

Besoeker

Senior Member
Location
UK
Still trying to understand. If I have A = 20A, B=20A, and C=0A, I get sqrt(400+400+0-400-0-0) = 20

Am I missing something (phase angles or harmonics)?
Or making it more complicated?

I suppose that the original post referred to a three wire centre tapped system.
This sort of arrangement:

singlephasepower14.jpg


If Ra and Rb are equal resistive loads the the neutral current would be zero.
Like this:

120-0-120atunity01.jpg


I made the currents slightly different to show some neutral current.

But suppose the loads have different power factors with Ia leading and Ib lagging you could get something like this:

120-0-120at0-501.jpg


In is greater than Ia and Ib.
 
Last edited:

jumper

Senior Member
Thought you might like that. :)

OT here and a bit political. Mods please forgive. I will drop it after this.

I will not ever recognize the British Union Jack until St. David of Wales cross is included.

I do not mean this as anything towards you Bes, it is directed at the English Crown and heraldry/design of the flag.

James I should have never accepted the crown. Scotland was a sovereign nation. Wales, isolated and small, OTOH was over run and conquered by Edward I and his hordes, never really had a chance.

It is 3:00AM and I am going off on British history, probably badly at that, on a electrical code forum. I gotta go to bed.

History 101 is over.
 

mivey

Senior Member
But suppose the loads have different power factors with Ia leading and Ib lagging you could get something like this:
.
I also think this thread is about a single-phase load but I recall you made a similar point when that formula for an ideal unbalanced three-phase circuit showed up in a different thread. I seem to recall resistance from some who wanted an easy answer but as you pointed out, the easy answer is hardly ever applicable.

FWIW, the correct methods are not really that hard so why not just calculate it the correct way to start with?
 

Besoeker

Senior Member
Location
UK
I also think this thread is about a single-phase load but I recall you made a similar point when that formula for an ideal unbalanced three-phase circuit showed up in a different thread. I seem to recall resistance from some who wanted an easy answer but as you pointed out, the easy answer is hardly ever applicable.

FWIW, the correct methods are not really that hard so why not just calculate it the correct way to start with?
I think the real shame is that it gets taught in the first place.
 