Calculating Power with Given Values
BatmanisWatching1987
NJ
Jr. EE
A balanced delta load consist of three 20∠25° impedance. The 60 Hz line voltage is 208 V (rms).
I got the following values using the information above
Phase Current = 10.4∠-25° A
Line Current = 18∠-55° A
Phase Voltage = Line Voltage = 208V
What is the correct Total Power
Since
P = (3)*Vp*Ip*cosθ = 3*208*10.4*cos(-25°) = 5882 W
P = √3*Vl*Il*cosθ = √3*208*18*cos(-55°) = 3720 W.
Why I'm I getting 2 completely different answers?
I can't solve the whole problem for you. But I will observe that you are treating the phase angle of all four voltages (phase voltages A, B, and C and line voltage) as zero. That is not correct. Phase voltages A, B, and C will differ from each other by 120 degrees, and I don't know what the angle of line voltage to phase voltage would be.
I thought for a Delta configuration, Line Voltage = Phase Voltage
190404-2243 EDT
BatmanisWatching1987:
You are blindly applying equations without understanding their derivation.
A solution to the problem is:
1. Line-to-line voltage is 208.
2. Current thru one line-to-line load is 208/20 = 10.4 A, that is voltage divided by impedance.
3. Need to know the series resistance of one line-to-line load. This is determined from the solution of a right triangle with one included angle of 25 deg, and a hypotenuse (impedance) of 20 ohms. The result is 20*cos 25 = 20*0.9063 = 18.13 ohms. This results from how phase angle is defined.
4. Power in one line-to-line load is I^2*R = 10.4^2*18.13 = 108.16*18.13 = 1960.9 watts. There are three of these so total power is 3*1960.9 = 5883 total watts.
There are some underlying assumptions. The waveforms are sinusoidal, and steady state in value, and loads are linear.
You can work back from this to determine a single equation to use, and then qualify that equation by defining all of the assumptions.
190404-2450 EDT
Your second approach is really one relative to assuming you know the impedance from line to neutral in a balanced wye load, but you don't. However, there is a transform equation that would allow you to determine this.
Fundamental in this second calculation for power in your second method (not the transform) is a determination of the line-to-neutral voltage which is based on cos 30 which happens to equal 1/2 sq-root of 3, and in turn how thru gyrations ends up as a sq-root of 3 in the numerator.
P3ø = (3)*Vp*Ip*cosθp = 3*208*10.4*cos(-25°) = 5882 W
θp=angle between EAB and IAB
P3ø = √3*Vl*Il*cosθL = √3*208*18*cos(-25°) = 5882 W.
θL=angle between IA and VA[VA it is a virtual voltage between terminal A and a virtual N]