BatmanisWatching1987
- NJ
- Jr. EE
... But one additional step, the problem statement says something about connecting 2 watt meters on lines A and B, which is confusing since watt meters must be connected to measure both voltage and current, so you would somehow need to connect the two watt meters to all 3 phases.
P = 3 * V(phase) * I(phase) * cos(theta).
theta is the angle between phase current and voltage.
V(phase)=202V
I(phase)=202/25=8.1A
P=3*202*8.1*cos(60)=2448W
There are many other ways to solve the problem but there are in fact just a couple of main equations manipulated in different ways.
How would I use, P = √3VLILcosθ
With, Ia = 13.995∠-90°
I thought you could use either P = √3VLILcosθ or P = 3 * V(phase) * I(phase) * cos(theta) interchangeable.
When would I know, which formula to use.
Just remember theta is always the angle between phase current and voltage. In other words theta is your impedance angle.
Thanks this will help me out a lot.
Correct me if I'm wrong,
For a Balanced 3 Phase Delta System, since Line Voltage and Phase Voltage are equal, and if the the impedance is given, we can use the phase current for theta to find the Total Power for 3 Phase Load, which was equal to 2.448 kW.
But, if we want to find the Single Phase Power we will use the line current angle, the power would be 0W? (Since the angle is 90 degrees)
I am not sure if I understand your question. Again, theta is you impedance angle; in this case (Zp=25<60 Ω) θ is 60 degrees. Where did you get 90 degrees? Load power always equals 3*|Iф|*|Vф|*cos(θ) where θ is the load impedance angle. Doesn't matter three phase Y, Δ or single phase. For single phase just remove the 3.
The lesson to be learned is the power factor angle to be used in problem(B) is the impedance angle of 60 degrees ie angle between phase voltage and phase current and not the angle between line voltage and line current.View attachment 22295
I am trying to solve Problem "B"
I got Ia = 13.995∠-90°. (Which is the Line Current = IL)
The power formula I am also using is, P = √3VLILcosθ
What is the correct value of "θ" should I be using?
In other problems, I always used the value of θ from the current angle.
The lesson to be learned is the power factor angle to be used in problem(B) is the impedance angle of 60 degrees ie angle between phase voltage and phase current and not the angle between line voltage and line current.![]()