Good morning to my electrical math wizards,
I have a 3-phase 500 kVA isolation transformer 480 delta fed by a EPC 500 kW inverter powered by a 1107 kWH battery, to 480 wye fed to switch gear. There is a 450 kW generator to charge the battery when solar is inadequate. In black start conditions, the generator breaker typically trips, unless I open the battery inverter breaker on the primary side of the transformer, then close the generator switch gear breaker, then close the transformer breaker.
The company that installed the equipment keeps discussing the need for a coordination study. But, it is my thoughts that the secondary, wye, side of the transformer may actually have a higher inrush current than the delta primary. I also think that while setting a longer delay on the generator may prevent the generator breaker from tripping, I don't want the generator being exposed to that current.
1. Are there reliable calculations that will provide the inrush current and the length of time the generator would be exposed to that current?
2. What is the least costly and most effective way of limiting the inrush current on the output side of the generator?
I have a 3-phase 500 kVA isolation transformer 480 delta fed by a EPC 500 kW inverter powered by a 1107 kWH battery, to 480 wye fed to switch gear. There is a 450 kW generator to charge the battery when solar is inadequate. In black start conditions, the generator breaker typically trips, unless I open the battery inverter breaker on the primary side of the transformer, then close the generator switch gear breaker, then close the transformer breaker.
The company that installed the equipment keeps discussing the need for a coordination study. But, it is my thoughts that the secondary, wye, side of the transformer may actually have a higher inrush current than the delta primary. I also think that while setting a longer delay on the generator may prevent the generator breaker from tripping, I don't want the generator being exposed to that current.
1. Are there reliable calculations that will provide the inrush current and the length of time the generator would be exposed to that current?
2. What is the least costly and most effective way of limiting the inrush current on the output side of the generator?