I removed 2 spot welders that were 480 volts single phase. Need to reinstall them in another location. One is 50 and the other is 150 KVA at 50% duty cycle. My question is, do you calculate it as single phase or 3 phase. Technically your pulling 2 legs from a 3 phase panel. Yet I removed 250 amp fuses and 4/0 wire at 90 degree which is rated for 260 amps for the 150 KVA. Yet if you calculate it as single phase you need at least 312.5 amps. KVA x 1000 divided by supply voltage. Divide that by 1.732 for 3 phase. Is there a different formula, or am I correct that the wire and fuses are undersized.