I am trying to figure out the correct kVA value to enter into an electrical panel schedule for various mechanical equipment based on the info given on mfg cut sheets. For example, the tech data sheet for a 3 phase split AC unit lists the following info:
My question is: How to calculate the correct value of kVA to use in the panel schedule?
Do I multiply 480V*(COMP RLA + OFM FLA)*1.732/1000 to get 3 phase kVA?
or do I get kVA by dividing the given kW by an presumed power factor (say 0.8)?
or....???
- Total power (kw) = 6.2
- Voltage = 460V/3P/60hz
- COMP 1 RLA = 9.7 (compressor rated load amps)
- COMP 1 LRA = 62 (compressor locked rotor amps)
- OFM (ea) WATTS = 325 (I have no idea what "OFM" stands for)
- OFM (ea) FLA = 0.8 (full load amps)
- MCA = 13.7 (min circuit amps)
- FUSE = 20 (max overcurrent device rating)
My question is: How to calculate the correct value of kVA to use in the panel schedule?
Do I multiply 480V*(COMP RLA + OFM FLA)*1.732/1000 to get 3 phase kVA?
or do I get kVA by dividing the given kW by an presumed power factor (say 0.8)?
or....???