OK, my next question is related to the blower unit - all I have there is hp (=1) and voltage (=480/3P). I believe the NEC table for 3 phase motors shows the FLA to be 2.1 (@460V). So to get the 3 phase kVA for that equipment I simply multiply (2.1)*(480)*SqRt(3)/1000 to get 1.745 kVA? Is that correct?
You are correct.
Don't get sucked into a debate about whether to use the nominal voltage (460) or the system voltage (480) for this calculation. Whatever voltage you use is wrong. The utility is allowed to swing from 85% to 110% of "Nominal." And "Nominal" is whatever they say it is. I've seen one utility use 480 and another use 460. And it WILL swing, usually lower in the summer and higher in the winter. Then don't forget about your feeder and branch circuit voltage drops. When it comes to load calcs, this stuff falls under the heading of "How many angels fit on a pin-head".
Just remember; S = I x E x 1.73 and don't bite your fingernails.