Given a 3-phase wye circuit (3 conductors and grounded neutral), with phase currents of L1=58A, L2=74A, L3=64A and N=12A, how does one compute the total current?
For simple calculation at unity (or equal) power factor...
If you want to do a calculation with unequal power factor, let me know...
Ohh!!! Just re-read your post...
There is no such thing as total current. It is what it is.
On the other hand, you can calculate total VA... or Watts if you know the power factors. Is that what you're looking for?
...With a 65kVA UPS (with 80% derated max current of 160A), I'm trying to determine how close to capacity I am on a per phase basis, assuming balanced load (which of course I don't have in this example). I know from a total load perspective, I'm at about 55% (of 80% derated capacity). What I'm trying to determine is what the max amp per phase limits are with a max total current of 160A....
Thanks for the replies. I know the formula for calculating neutral current, as well as other basic conversion formulas.
More detail:
With a 65kVA UPS (with 80% derated max current of 160A), I'm trying to determine how close to capacity I am on a per phase basis, assuming balanced load (which of course I don't have in this example). I know from a total load perspective, I'm at about 55% (of 80% derated capacity). What I'm trying to determine is what the max amp per phase limits are with a max total current of 160A.
TIA for any replies.
I'm having trouble understanding exactly what you are trying to do? As others have already said, these terms don't have any meaning. Here is a suggestion on nomenclature:What I'm trying to determine is what the max amp per phase limits are with a max total current of 160A. ....
What's with this "derated" capacity???...80% derated capacity...
I'm having trouble understanding exactly what you are trying to do? As others have already said, these terms don't have any meaning. Here is a suggestion on nomenclature:
Assuming 65kva, 208V Wye: Output current is 180A. Forget the "amps per phase". Forget the "total current". Those terms don't mean anything when discussing 3 phase.
For 3 phase balance load (fully loaded), put a clamp-on on each phase conductor, and each ammeter will read 180A. When you are asked what is the current? And you say 180A. You are saying the current is balanced and nominal 180A measured on each phase conductor.
For unbalance load, list the currents just the way you did, "phase currents of L1=58A, L2=74A, L3=64A and N=12A". That is perfect. There is no total current. They are vectors - if you add them, they better equal zero.
ice
What does it even mean?Given a 3-phase wye circuit (3 conductors and grounded neutral), with phase currents of L1=58A, L2=74A, L3=64A and N=12A, how does one compute the total current?
:thumbsup: Since power is not a vector, total power is completely meaningful, even though it is not necessarily the right way to check to see whether a given source can handle a given load configuration.It does not mean anything. I would love it if people would stop using the phrase "total current."
It does not mean anything. I would love it if people would stop using the phrase "total current."
Do you want to test it?One way:
58+74*cos(-120)+j74*sin(-120)+64*cos(120)+j64*sin(120). Compute it and check if it is equal in magnitude to neutral current value= 12 A.
If you are pleased, please do it on my behalf.Do you want to test it?