Hello folks.

I am trying to make sense of a pretty common industry practice for HRGs... the use of a zig-zag transformer to produce an artificial neutral.

For some context, existing ungrounded systems that would like to upgrade to high resistance grounded but lack a system neutral need an additional means to measure the fault current. One way to go about this is by deploying a zig-zag transformer that provides the required neutral, and therefore a means for the fault current to be measured through the grounding resistor.

Typically this is done with an individual 3-phase zig-zag transformer with no secondary winding (err, autotransformer?). With that being said, three single-phase transformers can also be wired to yield the same zig-zag setup, also resulting in an artificial neutral... some HRG vendors go about it this way. I am trying to better understand the setup and the individual transformers sizing + fault current magnitude at different parts of the circuit.

Please forgive the crude sketch, but assuming a fault current of 5A, is my logic correct in that each CPT only carries 1/3 the fault current?

PXL_20241213_201051058.MP.jpg

Each CPT is 480V Primary/240V Secondary, so doing a transformer sizing calc, my 1.67A "load" @ 240V would require at a minimum a 240V*1.67A = 400VA transformer. Since pulsing current is usually another 5A (for a total of 10A), let's say 800VA. Am I going about this the right way?

My questions:
1) Even though these are single-phase CPTs, they are wired in a 3-ph setup. Do I need to treat my calcs that same as a 3-ph setup and consider the 1.73 multiplier in my calcs?
2) Is the primary current on my CPTs actually 1.67A per primary? I do have a 2:1 transformer ratio between the primary and secondary of the CPTs so it could be that it's only .83A on the primary? I don't think so since this isn't a conventional use of a transformer, but I am having my reservations.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
In my experience it is rare to use 3 'off the shelf' transformers to build your own zig-zag configuration. I have always just ordered what I needed.

For off the shelf I have used wye-delta configurations instead of zig-zag.
 
Last edited:

MechEdetour

Member
Location
NY, USA
Occupation
Design Engineer
In my experience it is rare to use 3 'off the shelf' transformers to build your own zig-zag configuration. I have always just ordered what I needed.

For off the shelf I have used wye-delta configurations instead of zig-zag.
I will say that it is atypical, but some vendors do provide the 3 individual CPTs as their zig-zag solution. Some do it with a single 3-phase transformer, others do it the way I have shown in my sketch.

Coincidentally, and not sure how I missed it previously, but I just came across this blurb in Post Glover's application guide:

The KVA rating of each of the transformers should be equal to one-third the rated line-to-line voltage times rated ground current for continuous duty.

1734124620935.png

This is more or less in line with my calculation, but they say to use L-L voltage to determine transformer KVA. In my case I guess it would be 480V * (1/3) * 5A = 800VA. I would still like to understand why this is the case. From my sketch it seems that the primary and secondary of each CPT would see the same current.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
I've done _one_ self built zig-zag transformer. The coils all need to be the same voltage. You can't use 480:240 transformers, though you could use 480/240 : 240/120 transformers wired for 240 : 240V.

Jonathan
 

MechEdetour

Member
Location
NY, USA
Occupation
Design Engineer
I've done _one_ self built zig-zag transformer. The coils all need to be the same voltage. You can't use 480:240 transformers, though you could use 480/240 : 240/120 transformers wired for 240 : 240V.

Jonathan
How does that work? So in that case it wouldn't matter if the system voltage is 600V delta or 480V delta? I understand that these CPTs would not be used in a conventional way, and maybe that's why it works the way you describe.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
How does that work? So in that case it wouldn't matter if the system voltage is 600V delta or 480V delta? I understand that these CPTs would not be used in a conventional way, and maybe that's why it works the way you describe.
The secondary winding voltage needs to be the same voltage as the primary winding in order to be used as a zig-zag.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
How does that work? So in that case it wouldn't matter if the system voltage is 600V delta or 480V delta? I understand that these CPTs would not be used in a conventional way, and maybe that's why it works the way you describe.
The secondary winding voltage needs to be the same voltage as the primary winding in order to be used as a zig-zag.

You need three transformers, each with two of the same voltage coils on the same core, wired in the zig-zag configuration.

The coil voltage rating needs to be high enough that the coils are not saturated during normal operation. If the individual coil voltage is X, then the L-L voltage rating of the zig-zag connection is 3X. So 240V coils should be more than fine for a 480V system.

Jonathan
 

MechEdetour

Member
Location
NY, USA
Occupation
Design Engineer
If the individual coil voltage is X, then the L-L voltage rating of the zig-zag connection is 3X. So 240V coils should be more than fine for a 480V system.
So in that case it should be adequate for the 600V as well, correct?

Since only coil voltages seem to be relevant here, how does the kVA size come into the picture? For my example above where there would be 5A of fault current and even 10A flowing @ a pulsing rate (for locating fault with a pulsing circuit), how does this translate into calculating kVA size? Is it the same as if I had 5A-10A of load current?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
During a fault, 1/3 current flows in each leg of the system. So if you have a 10A fault current, you have 3.33A in each coil.

Take the current * the coil voltage rating to get the VA rating of the coil. In your case 240V * 3.33 = 800. In general a 1 kVA transformer can carry 1 kVA on the primary _and_ 1 kVA on the secondary, so in your case you would need 3 pieces of 0.8 kVA 240V:240V transformers to carry 10A of fault current on a continuous basis.

Given your 5A continuous, 10A pulsed, you could get away with smaller transformers, on the other hand it doesn't pay too much to try to exact size these transformers; they are so small that the cost of installation will vastly exceed the difference between 500VA or 750VA or 1kVA units.

-Jonathan
 

MechEdetour

Member
Location
NY, USA
Occupation
Design Engineer
During a fault, 1/3 current flows in each leg of the system. So if you have a 10A fault current, you have 3.33A in each coil.

Take the current * the coil voltage rating to get the VA rating of the coil. In your case 240V * 3.33 = 800. In general a 1 kVA transformer can carry 1 kVA on the primary _and_ 1 kVA on the secondary, so in your case you would need 3 pieces of 0.8 kVA 240V:240V transformers to carry 10A of fault current on a continuous basis.

Given your 5A continuous, 10A pulsed, you could get away with smaller transformers, on the other hand it doesn't pay too much to try to exact size these transformers; they are so small that the cost of installation will vastly exceed the difference between 500VA or 750VA or 1kVA units.

-Jonathan
Thank you @winnie for the explanation.

May I ask another question?

Referring to the post you made previously,
I've done _one_ self built zig-zag transformer. The coils all need to be the same voltage. You can't use 480:240 transformers, though you could use 480/240 : 240/120 transformers wired for 240 : 240V.

Jonathan

A 480/240 : 240/120 CPT would be wired such that it's used in it's 240 : 240 form. The primary however would still be physically connected to a 480V delta system (as shown in my initial sketch), wouldn't it?. Is it fair to say that the only reason that would be allowed is because the primary is suitable up to 480V (ie. insulation, etc. is rated for it)? Or would this particular CPT wired for 240 : 240 only be suitable for a system that is rated 240V?

These CPTs are only being used to produce a neutral so I am trying to make sense of all the nuances.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The primary however would still be physically connected to a 480V delta system (as shown in my initial sketch), wouldn't it?
Technically there is no primary or secondary when you are dealing with autotransformer configurations. Instead, they have High and Low voltage sides, although factory built units may list primary and secondary on their nameplates. Typically a zig-zag transformer would have maximum voltage rating.

A DIY transformer configuration will require a DIY label.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Thank you @winnie for the explanation.

May I ask another question?

Referring to the post you made previously,


A 480/240 : 240/120 CPT would be wired such that it's used in it's 240 : 240 form. The primary however would still be physically connected to a 480V delta system (as shown in my initial sketch), wouldn't it?. Is it fair to say that the only reason that would be allowed is because the primary is suitable up to 480V (ie. insulation, etc. is rated for it)? Or would this particular CPT wired for 240 : 240 only be suitable for a system that is rated 240V?

These CPTs are only being used to produce a neutral so I am trying to make sense of all the nuances.

You are correct, the transformer will need a voltage to ground insulation rating suitable for 480V. Most small transformers use 600V insulation systems, but it certainly pays to check.

This same issue is seen with buck/ boost transformers where a 24V coil might be electrically in series with a 208V coil.

Jonathan
 