kda3310
- Dry Prong, Louisiana
(This is a hypothetical situation) I have two 40 horse motors 50 feet from the MCC. They will be a continuous load. They are running through a boiler room that is 120°F. They will be running in the same conduit. How do I calculate the wire size I need to run?
40H Motor is 52Amps
52 x 1.25 for continuous load is 65Amp
Now for having 6 current carrying conductors I have to multiply that by 80%. But do I multiply that by the 52 amps or by the 65 amps?
It will be the same question for the ambient temperature. Which amperage do I multiple by?
40H Motor is 52Amps