garylr

Member
I'm in the process of sizing power cords for our motor operated equipment. I have calculated voltage drops and have calculated my cord AWG using a Voltage drop rule of 5%of the source voltage. My co-worker has requested I calculate voltage drop using Locked-rotor amps as well as FLA for the motor.

Is there any justification to calculating wire size with Locked rotor amps?? My co-worker said he wants to make sure the motor will start. This does not make sense to me? AS long as the motor is supplied with votage within 10% of nameplate rating.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: calculating wire size for motor load

You certainly could use LRA. But there is no reason to do so. It would be overkill, and overly expensive.
 

bphgravity

Senior Member
Location
Florida
Re: calculating wire size for motor load

Locked-rotor currents would be more of a concern when sizing the ground-fault / short-circuit protection devices rather than sizing the supply conductors. I would think the 5% total drop you have already worked in will be sufficient for both the starting and running of the motor.
 