Unless I miss the point you are trying to make, you are wrong. The code requires 1 laundry circuit for any and all the outlets required in section 210.52(F) It clearly does not require a circuit for multiple laundry rooms or locations in a single residence. The word laundry room is not used in any of the applicable sections. Regarding the load, and having enough capacity for it in a dwelling unit, in the 20 plus years I have been doing electrical work, I have never known a main breaker in a dwelling unit to trip from an overload condition, nor have I ever felt a main breaker getting too hot from an overload condition, nor have I ever put an ammeter on a house feeder andfound it to be drawing over current from an overload condition. I do not think that I would worry about an overload on the main because someone was running two washing machines in the same house. The point here is that the NEC allows you to feedmore than one laundry receptacle outlet from the one code required laundry circuit. The washing machine is not a fixed appliance therefore it is not required to be included in the load calculations other than the generic requirement not to overload any circuit. No matter whether you think it should be included. The code does not require it.