My customer has four 240 volt, 2000 watt baseboard heaters that they want to install. The service is 120/208 three phase. What will be the actual connected load of the heaters. I am calculating P/E=I, P=I^2 x R solving for R, E/R=I, then I^2 x R= VA..... I am doing this correctly? I don't think I am I am just not seeing it. Can somebody help please?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Your 2000 watt 240 volt heaters would be about 1501 watts on 208 or 7.2 amps.
Total load would depend on which phases you use to connect.
2000* (208/240)?
 

Smart $

Esteemed Member
Location
Ohio
Total load would depend on which phases you use to connect.
To elaborate on that, four identical 1? loads cannot be balanced on a 3? system. He either has to have other loads unbalanced to offset, or has to compensate for the unbalance in the conductor sizing and OCPD determination... that is, if calculating a completely new supply. If an existing supply, he must determine if said supply has the capacity on a per line basis, or revise so that it does.
 