Calculation Question

Status
Not open for further replies.

Electric76

New member
Is a vent light bathroom fixture considered fasted in place and able to apply the 75% demand factor of 220.53? Or is this included in the 3va per sqft general lighting load?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
IMO, the bath fan is not an appliance and should not even be considered as a 75% reduction. That being said I guess one could make a case for it
 
Status
Not open for further replies.
Top