E Electric76 New member Location Des Allemands, LA Jul 28, 2017 #1 Is a vent light bathroom fixture considered fasted in place and able to apply the 75% demand factor of 220.53? Or is this included in the 3va per sqft general lighting load?
Is a vent light bathroom fixture considered fasted in place and able to apply the 75% demand factor of 220.53? Or is this included in the 3va per sqft general lighting load?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jul 28, 2017 #2 IMO, the bath fan is not an appliance and should not even be considered as a 75% reduction. That being said I guess one could make a case for it
IMO, the bath fan is not an appliance and should not even be considered as a 75% reduction. That being said I guess one could make a case for it
L lielec11 Senior Member Location Charlotte, NC Occupation Electrical Engineer (PE) Jul 29, 2017 #3 I would typically include that in the 3VA/ft2 load. Most of these exhaust fans or exhaust/light combos use a fan under 100W.
I would typically include that in the 3VA/ft2 load. Most of these exhaust fans or exhaust/light combos use a fan under 100W.