Enhnhnhnhnht!!! Incorrect answer.Refresher![]()
Calculate the neutral current in a 208Y/120 volt 3 phase, 4 wire system when he current in phase A is 40Amps, in phase B is 20 Amps and in phase C is 30 Amps.![]()
1 answer I can come up with by manipulating the loads is
1- 20 amp 3 phase load
1- 10 amp 208 volt single phase load connected A to C
1- 10 amp 120 volt single phase load
gives you 10 amps neutral current.
My guess is that is not the answer you were looking for.
I should have stipulated
the first 2 loads have no neutral connection,
only the 10 amp 120 volt load
1 answer I can come up with by manipulating the loads is
1- 20 amp 3 phase load
1- 10 amp 208 volt single phase load connected A to C
1- 10 amp 120 volt single phase load
I should have stipulated the first 2 loads have no neutral connection, only the 10 amp 120 volt load
There isn't any adding required for the neutral conductor. The loads only add, vectorially, at the line connection.That still doesn't work.
For example, the current in the 120V single phase load won't be in phase with the current in the 208V single phase load so you can't just add them arithmetically.
If anyone reading that thread wants to download my Excel neutral calculator, which allows for entry of and accounts for power factor, go to the following post:http://forums.mikeholt.com/showthread.php?t=93575
Check out this thread. Lot of smart guys on this forum.
The loads also add vectorially in the neutral. That's how you end up with zero in the neutral if you have a balanced load. Suppose you have 1A at zero, 1A at 2Pi/3, and 1A at 4Pi/3.There isn't any adding required for the neutral conductor. The loads only add, vectorially, at the line connection.![]()
I already have one I made earlier, thanks. That's how I generated the waveforms I put in post #9.If anyone reading that thread wants to download my Excel neutral calculator, which allows for entry of and accounts for power factor
The loads also add vectorially in the neutral. That's how you end up with zero in the neutral if you have a balanced load. Suppose you have 1A at zero, 1A at 2Pi/3, and 1A at 4Pi/3.
Then:
Ia = 1
Ib = -0.5 - jsqrt(3)/2
Ic = -0.5 + jsqrt(3)/2
In = Ia + Ib + Ic
= 0
QED
But my point was that masterinbama could only have arrived at the 40A for Ia by arithmetic addition of the currents he gave (20+10+10)
I agree with the 17.3A given by both Dexie and Infinity.
But only for the specific case where the power factor on all three phases is exactly the same i.e. the currents are phase displaced from each other by 120degE.
In the more general case where the power factors are not the same you could get a quite different answer. The example below still has 40A, 20A and 30A for A,B, and C respectively but the neutral current (black) is a little over 50A rms.
![]()