Calculate the neutral current in a 208Y/120 volt 3 phase, 4 wire system when he current in phase A is 40Amps, in phase B is 20 Amps and in phase C is 30 Amps.:)
 
You are asking homework or study questions and we will not just provide you with answers, you must show your answers first and how you arrived at them then we will point you in the right direction.


Roger
 
Calculate the neutral current in a 208Y/120 volt 3 phase, 4 wire system when he current in phase A is 40Amps, in phase B is 20 Amps and in phase C is 30 Amps.:)

1 answer I can come up with by manipulating the loads is

1- 20 amp 3 phase load

1- 10 amp 208 volt single phase load connected A to C

1- 10 amp 120 volt single phase load

gives you 10 amps neutral current.

My guess is that is not the answer you were looking for.
 
1 answer I can come up with by manipulating the loads is

1- 20 amp 3 phase load

1- 10 amp 208 volt single phase load connected A to C

1- 10 amp 120 volt single phase load

gives you 10 amps neutral current.

My guess is that is not the answer you were looking for.

I think that your logic is incorrect. I came up with 17.3 amps.
 
Squrt ( Ia^2+Ib^2+Ic^2)-(Ia*Ib+Ib*Ic+Ic*Ia)

I=amps
a, b, and c = the 1st, 2nd, and 3rd phase amperage respectively
^2 = squared
Sqrt = after all is done you take the square root of the answer.

I get the square root of 300 = 17.3
 
I agree with the 17.3A given by both Dexie and Infinity.
But only for the specific case where the power factor on all three phases is exactly the same i.e. the currents are phase displaced from each other by 120degE.
In the more general case where the power factors are not the same you could get a quite different answer. The example below still has 40A, 20A and 30A for A,B, and C respectively but the neutral current (black) is a little over 50A rms.

three-phase02.jpg
 
1 answer I can come up with by manipulating the loads is

1- 20 amp 3 phase load

1- 10 amp 208 volt single phase load connected A to C

1- 10 amp 120 volt single phase load


I should have stipulated the first 2 loads have no neutral connection, only the 10 amp 120 volt load
 
I should have stipulated
the first 2 loads have no neutral connection,
only the 10 amp 120 volt load

MasterInBama,
alias Perry Mason, "stipulate"!

The OP "stipulated" a WYE circuit.

Try this on any combo:

Square root of
( (Ia^2)+(Ib^2)+(Ic^2) )-( (Ia*Ib)+(Ib*Ic)+(Ic*Ia) )

with the "stipulation" that
if a line is not connected to neutral,
then that line current is zero.

:)
 
Last edited:
1 answer I can come up with by manipulating the loads is

1- 20 amp 3 phase load

1- 10 amp 208 volt single phase load connected A to C

1- 10 amp 120 volt single phase load


I should have stipulated the first 2 loads have no neutral connection, only the 10 amp 120 volt load

That still doesn't work.
For example, the current in the 120V single phase load won't be in phase with the current in the 208V single phase load so you can't just add them arithmetically.
 
That still doesn't work.
For example, the current in the 120V single phase load won't be in phase with the current in the 208V single phase load so you can't just add them arithmetically.
There isn't any adding required for the neutral conductor. The loads only add, vectorially, at the line connection. ;)
 
There isn't any adding required for the neutral conductor. The loads only add, vectorially, at the line connection. ;)
The loads also add vectorially in the neutral. That's how you end up with zero in the neutral if you have a balanced load. Suppose you have 1A at zero, 1A at 2Pi/3, and 1A at 4Pi/3.

Then:
Ia = 1
Ib = -0.5 - jsqrt(3)/2
Ic = -0.5 + jsqrt(3)/2

In = Ia + Ib + Ic
= 0

QED
;)

But my point was that masterinbama could only have arrived at the 40A for Ia by arithmetic addition of the currents he gave (20+10+10)
 
If anyone reading that thread wants to download my Excel neutral calculator, which allows for entry of and accounts for power factor
I already have one I made earlier, thanks. That's how I generated the waveforms I put in post #9.
:)
 
The loads also add vectorially in the neutral. That's how you end up with zero in the neutral if you have a balanced load. Suppose you have 1A at zero, 1A at 2Pi/3, and 1A at 4Pi/3.

Then:
Ia = 1
Ib = -0.5 - jsqrt(3)/2
Ic = -0.5 + jsqrt(3)/2

In = Ia + Ib + Ic
= 0

QED
;)

But my point was that masterinbama could only have arrived at the 40A for Ia by arithmetic addition of the currents he gave (20+10+10)

My first post was a little vague. Allow me to add to it

1 answer I can come up with by manipulating the loads is

1- 20 amp 3 phase load with no neutral connection

1- 10 amp 208 volt single phase load connected A to C with no neutral connection

1- 10 amp 120 volt single phase load

gives you 10 amps neutral current.
 
I agree with the 17.3A given by both Dexie and Infinity.
But only for the specific case where the power factor on all three phases is exactly the same i.e. the currents are phase displaced from each other by 120degE.
In the more general case where the power factors are not the same you could get a quite different answer. The example below still has 40A, 20A and 30A for A,B, and C respectively but the neutral current (black) is a little over 50A rms.

three-phase02.jpg

When I first read the OP, and did a quick calculation in my head, my mind said....worst case, 50A on the neutral.

Try as I might, I cannot repeat the calculation.:roll:

I had either a flash of brilliance, or a moment of delusion.:D

steve
 