california 3-way

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: california 3-way

Wayne,
noxx did not say that the screw shell is hot in the 3 way shown on the drawing above his post. He said it would be hot in the 3 way ciruit that I described in my post. Go to the link in Roger's post of 9/20 at 10:12 am. The screw shell is the female threads on the socket that the light bulb screws into.
Don
 

ronaldrc

Senior Member
Location
Tennessee
Re: california 3-way

Bennie I think a fourway would work if you put it between the light return and the hot?

And don't forget about our barbed fence and pipe wire we can always work them in. :D

Ronald

[ September 22, 2003, 03:47 PM: Message edited by: ronaldrc ]
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: california 3-way

Bennie,

I like the name Travelling Bus Threeway. Very clear. It's the first time I've heard it.

Here, consider this fourway setup of the travelling bus.
img33.jpg
 

bennie

Esteemed Member
Re: california 3-way

Very good Al and Ronald. This is an interesting circuit.

The installation was to allow the use of two, 2 conductor cables between the switches and be able to extend the circuit to another room.

One cable was the line and neutral. The other was to provide the switching.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: california 3-way

My Mother's garage has the very setup you describe, Bennie. Her house was built in 1953.

Of course, today's 300.3(B) prohibits the use of two two conductor cables to create this. If an NM cable is used it has to be a four conductor plus ground.

[ September 22, 2003, 11:05 PM: Message edited by: al hildenbrand ]
 

noxx

Senior Member
Re: california 3-way

That's correct Don, Roger's link is the switching arrangement I was describing as a "Coast" 3way, apparently the slang varies to include all manner of oddball switching.

A couple of the drawings that have popped up here would not have occurred to me tho, good to have them on my "things to look for" list.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: california 3-way

Al,
Of course, today's 300.3(B) prohibits the use of two two conductor cables to create this. If an NM cable is used it has to be a four conductor plus ground.
I believe that 300.3(B)(3) would permitt that installation using 2 conductor NM as long as you comply with 300.20 for the box entries.
Don
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: california 3-way

Hmmmm. . .interesting! (As scales fall from eyes) Thanks, Don.

[ September 23, 2003, 10:45 AM: Message edited by: al hildenbrand ]
 

roger willis

Member
Location
Texas
Re: california 3-way

Trace the circuit out and you will see why. When you have the 4-way switches in a one position and the lights are on, turn the lights off with the 4-way on the right and then try to turn the lights back on with the 4-way on the left.
 

roger willis

Member
Location
Texas
Re: california 3-way

Al, I may be wrong, but I don't think so. Some of you others help us out and see if you see the samething I'm seeing.

Roger
 

roger willis

Member
Location
Texas
Re: california 3-way

Al, to explain it a little better. Leave the 3-way switches in the position that you have them in now. With the 4-way on the left, have it in the cross connect position. With the 4-way on the right, put it in the straight thru position and the lights are on. Turn the lights off with the 4-way on the right. Now try to turn the lights back on with the 4-way on the left.

Roger
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: california 3-way

Roger,

When the right fourway switches the lights off, the unswitched hot conductor (on a traveller between fourways) is connected to the right threeway common. The left fourway is also connecting the unswitched hot to the left common. So when the left fourway is switched from crossconnect to straight through, the energized traveller between the left threeway and the left fourway is connected to the "switch leg traveller" between the fourways.

Clear as mud. . .but accurate, I think.

In my mind, this is the really fun, but odd thing about this switch loop. . .on several combination of switch settings the current has to do a looooonngg loop de loop.

Heh! Should have left well enough alone. Re-Editted to follow your exact statement

[ September 23, 2003, 11:35 AM: Message edited by: al hildenbrand ]
 

roger willis

Member
Location
Texas
Re: california 3-way

Ok Al, I see it, I was wrong as usual. Yes, that is quite a loop-te-loop. I just missed seeing it.
Sorry about that.

Roger
 

ronaldrc

Senior Member
Location
Tennessee
Re: california 3-way

I planted the seed that a fourway would work if inserted between the hot and the light return on this traveling bus switch. Well Roger I think this is the same circuit that Al drew and if so you are right it won't work.

I inserted 1 fourway in and it screwed the whole thing up. Follow the orange to get a complete circuit.Dam its getting hard to type with all these fingers missing.

:eek:

[ September 23, 2003, 06:20 PM: Message edited by: ronaldrc ]
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: california 3-way

Ronald,

I believe that if you move L1 to the black traveller on the barn side of the fourway, it will work.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: california 3-way

Also,

The black condutor attached to the light at the house needs to be connected at the fourway to the orange wire on the barn side of the fourway.
 

ronaldrc

Senior Member
Location
Tennessee
Re: california 3-way

Al I'll try that after while when I said my layout would work it was just a huch I didn't try it. Your circuit might be different I have looked at it good yet.

Thanks:Ronald
 