chester7477
Member
I am calculating a service for a new campground according to article 551-72 and table 551-73 and after derating my calculation it seems to be too low.
10-50amp sites (9600va ea.) 96000va
33-30amp sites (3600va ea.) 118800va
total 214800va
demand factor 41%
88068va/240v =
367amps
600 amp service
Is this correct?
10-50amp sites (9600va ea.) 96000va
33-30amp sites (3600va ea.) 118800va
total 214800va
demand factor 41%
88068va/240v =
367amps
600 amp service
Is this correct?