- Wisconsin
- PE (Retired) - Power Systems
I did, so you might as well.Stealing that one![]()
All to many people make this more of an issue than it really is. They zero in on a breaker being 80% rated when that really isn't the issue at all.Now I'm even more confused.
I'm inclined to think that, if there is significant voltage drop across the closed contacts of a breaker, it won't survive long.
That was me... and I was straining my brain when writing that post to try to remember that exact saying....
Along the lines of what Templdl said: when you hear hoof beats think of horses, not zebras.
I agree. When you have too much resistance in the wire and it drops the voltage, the heat from that resistance is spread out over the entire length of the wire, so the likelihood of it causing noticeable problems is minimal. But when you have a significant voltage drop at a termination or a set of contacts, ALL of the heat from that resistance is expressed right there. The device fails in an obvious and quick manner. Bottom line if the CB was causing a 15% voltage drop, it would be smoking.
The 100% rated breaker is used in the same way except that the loads is calculated as 100%+100% 90degC rated wire must be used and sized to carry that load. The 100% breaker is simply sized to protect that wire and installed per the manufacturers instructions.
I am not familiar with actually using 100% rated breakers, but do not believe you must use 90oC conductor unless the listing of the breaker requires it.
You never, ever, use the 90?C columns when you terminate at any non-'ANSI switchgear' overcurrent device.
Due to the extra heat of a 100% device, UL listing requires 90?C conductors sized used the 75?C columns.
Yes, I overlooked the statement that 90degC must be used but applied at 75degC. Standard breakers depend on the wire acting like a heat sink taking heat away from the breaker. With 100% rated breakers and the associated wire sizing requirements you loose that heat sink advantage and the wire is more apt to add heating of some degree to the breaker which leads to the fact that 100% rated breakers have SS trip units.You never, ever, use the 90?C columns when you terminate at any non-'ANSI switchgear' overcurrent device.
100% rated device produce tons of heat.Why is there extra heat there? This concept kind of goes against what I thought I knew about this - the fact that a standard device uses the conductor as a heat sink but a 100% device does not.
The normal heat sink effect is what requires the larger 75?C conductor size. The extra heat is what causes the need for the 90?C insulation (similar to the 90?C insulation requirement for fixtures).
It doesn't.The fact that it produces more heat would make sense for requiring 90?C insulation, but I still can't get around the fact that if it produces more heat why the NEC would allow smaller sized conductor.
If minimum conductor size must be 125% of load how can you say a larger conductor is not required. Then you say the 100% rated device creates more heat, but it does not require the conductor to have an ampacity of 125% of load.It doesn't.
The conductor must be sized using the 75?C columns @ 125% loading, just like with any other protective device.
Remember, up to three hours the loading and the conductors can be the same for both a 100% and a standard (i.e. 80%) breaker.
So the difference is with the 25% adder to the protective device rating for 'continuous' loads. This is where the higher temp insulation comes into play as well as the 100% rated device being mounted in an enclosure that has greatly increased airflow to help manage the extra heat.
Unless specified by instructions, I don't see the NEC requiring that. For branch circuits, 210.19(A)(1) permits sizing before the application of adjustment or correction factors, while the Exception thereto permits ampacity sizing at 100% value (i.e. both continuous and non-continuous at 100%). For feeders, 215.2(A)(1) mimics the preceding....
Regardless what I may have posted, in a sleep deprived state, the above is correct.:ashamed1:For branch circuits, 210.19(A)(1) permits sizing before the application of adjustment or correction factors, while the Exception thereto permits ampacity sizing at 100% value (i.e. both continuous and non-continuous at 100%). For feeders, 215.2(A)(1) mimics the preceding.