Bea said:1-AHJ may determine the meter is a part of the raceway system as described in OP 230.7
Bea said:Meter combs have barriers that seperate unfused from fused and are listed for the purpose and the OP did not say he had meter comb just meter Thank You
Bea said:I would just like to ask the question would you run a branch circuit/feeder thru a meter enclosure that contains unfused conductors and if not why would you suggest it to someone else.
Jeffnmoe@comcast.net said:NEC 230.7 is clear in my eyes, NO BRANCH CONDUCTORS IN SERVICE RACEWAY which includes the meter fitting.
230.7 Other Conductors in Raceway or Cable. Conductors other than service conductors shall not be installed in the same service raceway or service cable.