181127-1004 EST
Noswad4:
Quickly rereading this whole thread I think your question is:
Can I control an electrical generator, AC or DC, to dump energy into the electrical grid based upon some signal, your turbine output pressure. The answer is probably yes.
How can you control electrical power flow in a system? By changing a voltage or current.
From your various comments and questions it appears you want to dump electrical power into the electrical grid system. To make things simple consider a DC system. To a pair of electrical terminals on the grid those terminals looking toward the grid appear to have the characteristics of a very large battery. This means the grid looks like an ideal constant voltage source with some small internal impedance, electrical resistance.
I can remove power from the grid by placing a load electrical resistance on the two terminals. So by my choice I will call this a positive current flow. This current flows from the voltage source thru its internal resistance to my external resistive load. There is a voltage drop across the internal resistance, and a power dissipation in that internal resistance, and externally there is a voltage drop across my load resistance, and its power loss. One wants to make that internal power loss low compared to the load power. The sum of the two voltage drops has to equal the voltage of the ideal constant voltage source.
Keep in mine that the grid is very large compared to what I do at the load terminals.
Next shift gears and create an energy source external to the grid. This source will consist of a variable voltage source and its own fixed internal electrical resistance.
Connect the external energy source to the two grid terminals.
If the external voltage is less than the grid voltage, then the external energy source is really a load, and just like the resistive load is receiving energy from the grid. Under these conditions it is not an energy source.
Adjust the external voltage source to equal the grid voltage. No current flows. Thus, no energy transfer.
Adjust the external voltage to a value higher than the grid voltage. Now current flows into the grid as does energy. The amount of current flow is the voltage difference between the two voltage sources divided by the sum of the two internal impedances (resistances).
The output power from the external source is its internal voltage times said current. The power into the grid is the grid internal voltage times said current. The inefficiency is in the power loss in the two internal resistances.
By adjusting the internal voltage of the external power source you change the amount of power flow to the grid from the external source.
To control power flow you do not change the electrical resistance of the generator, but rather you change its internal source voltage or current. With any reasonable set of conditions you can use electronic circuitry to do this.
.
181127-1334 EST
JFletcher:
Works the same way with AC. For maximum power transfer into the AC grid you want the current going in to be in phase with the voltage. Maximum power transfer (real power) as I used it here is mean't to describe how the phase angle of the current is related to the grid voltage where current magnitude is a constant.
In an AC power distribution system you want the current to be as much in phase with the voltage as possible to reduce wasted power in the I^2*R distribution losses. Any out of phase current is heating wires, etc, without doing useful work in the destination load.
I would not consider frequency an issue other than you need matching and synchronized waveforms.
.
181127-2441 EST
JFletcher:
I don't have direct experience tying a large alternator to the grid. But even a few megawatt unit is peanuts compared to the grid. The impedance into the grid is more of a factor. So your connection to the grid won't do much to the grid. Its frequency will stay the same, as will its internal equivalent voltage.
Other than for some form of small AC generator your generator can be considered a DC field excited alternator/synchronous motor. Whether it is a generator or motor is a function of the direction of energy flow. Once connected the motor/generator will run at line synchronous speed. For example exactly 1800 RPM on 60 Hz. Other possibilities at 60 Hz are 3600, 1200, etc.
If you have two voltage sources that are exactly the same. and connect them in parallel, then no current flows. If they are not the same voltage, then a large current can flow limited only by the impedance between them and the voltage difference.
When connecting one voltage source in parallel with another you want them matched to avoid large mechanical and electrical disturbances.
The alternator must run at AC line frequency. Mechanical and electrical phase angle might lead or lag, and internal equivalent voltage must be higher to force energy into the grid.
.
181127-1004 EST
Noswad4:
Quickly rereading this whole thread I think your question is:
Can I control an electrical generator, AC or DC, to dump energy into the electrical grid based upon some signal, your turbine output pressure. The answer is probably yes.
How can you control electrical power flow in a system? By changing a voltage or current.
From your various comments and questions it appears you want to dump electrical power into the electrical grid system. To make things simple consider a DC system. To a pair of electrical terminals on the grid those terminals looking toward the grid appear to have the characteristics of a very large battery. This means the grid looks like an ideal constant voltage source with some small internal impedance, electrical resistance.
I can remove power from the grid by placing a load electrical resistance on the two terminals. So by my choice I will call this a positive current flow. This current flows from the voltage source thru its internal resistance to my external resistive load. There is a voltage drop across the internal resistance, and a power dissipation in that internal resistance, and externally there is a voltage drop across my load resistance, and its power loss. One wants to make that internal power loss low compared to the load power. The sum of the two voltage drops has to equal the voltage of the ideal constant voltage source.
Keep in mine that the grid is very large compared to what I do at the load terminals.
Next shift gears and create an energy source external to the grid. This source will consist of a variable voltage source and its own fixed internal electrical resistance.
Connect the external energy source to the two grid terminals.
If the external voltage is less than the grid voltage, then the external energy source is really a load, and just like the resistive load is receiving energy from the grid. Under these conditions it is not an energy source.
Adjust the external voltage source to equal the grid voltage. No current flows. Thus, no energy transfer.
Adjust the external voltage to a value higher than the grid voltage. Now current flows into the grid as does energy. The amount of current flow is the voltage difference between the two voltage sources divided by the sum of the two internal impedances (resistances).
The output power from the external source is its internal voltage times said current. The power into the grid is the grid internal voltage times said current. The inefficiency is in the power loss in the two internal resistances.
By adjusting the internal voltage of the external power source you change the amount of power flow to the grid from the external source.
To control power flow you do not change the electrical resistance of the generator, but rather you change its internal source voltage or current. With any reasonable set of conditions you can use electronic circuitry to do this.
.
Other than frequency, there are necessary conditions that must be met for a successful synchronization of generator to the grid.
Voltage magnitude of the generator must be equal to the grid and we all know that. Meaning the sinusoidal voltage of the grid.
Sustained voltage differential of the two systems could create havoc on the generator —being that the grid has more power to go around with.
If the generator voltage is too high the generator will put out large MVAR (mega volt amp reactive.) which could cause generator to get overexcited and therefore overheating occurs.
Inversely, when generator voltage magnitude is too low, the MVAR will be absorbed and the generator becomes underexcited.
Now, since we are mostly focused on the frequency, this is by no means a small fry to ignore.
An elephant in the room if you will.
The sinusoidal frequency of the generator must be the same as the grid.
As one poster had alluded to an instrument that shows whether the generator and the grid are in the process of synchronizing themselves, this is called synchroscope. When the two systems are not synchronized the synchroscope will keep spinning.
When the two systems reach synchronicity it (synchroscope) will stop at 12:00 oclock that is also zero. This is the moment when you throw the switch on.
Throwing the switch before they get synchronized will cause the generator to suffer from being out of step and subsequently behave like a motor—not to mention the stator and rotor would be slipping. A potential destructive force.
An old-school way of checking sychronicity is using a light bulb. When there is voltage differential the bulb is lit—when the bulb goes dim synchronicity is achieved.
The same destructive force would be enforced upon the generator when it is running too fast. When this happens the grid will try to slow it down.
On the other hand running the generator too slow will prompt the grid to speed it up with the same destructive result.
Phase angle and phase sequence are also important considerations when synchronizing generator to the the grid. Details of which would be for another discussion.
These problems had been overcome with the introduction of mercury-arc valves (a glorified term for rectifier) which are now obsolete with the arrival of solid state GTOs (gate turn off thyristors) and IGBTs for high voltage inverters.
Generator voltage is first rectified to DC and then inverted to AC for ease of synchronization.
We are using this strategy in our California PACIFIC INTERTIE that supplies power to the largest municipal owned utility company (LADWP).
Myspark:
Could you elaborate on how wind turbines solve this issue when the blades spin at different speeds?