To Besoeker's point, transformer "ratings" are about the transformer operating within its design limits in terns of heat rise, so if you can decrease the heat rise, you can often increase the capacity of the transformer. But that only works for transformers DESIGNED to have added cooling, i.e. OA vs FA cooling on
OIL FILLED transformers. Rather than explain it all again, you can read this older thread.
Just curious to find out what OA stands for on older transformers, this isn't a homework assignment its 1st to answer the right answer in my class gets $5 bucks lol. I been googling and been getting closer to the right answer but I need to know what it stands for.
forums.mikeholt.com
But for "dry type" transformers that we typically see in distribution equipment, the rating
is the rating. So unless it specifically STATES a rating higher than it does, you would be in violation of 110.3(B) if you tried to use it that way. However, transformers have a TEMPORARY OVERLOAD capability without being damaged based on NEMA design criteria as follows:
- 200% nameplate load for one-half hour
- 150% load for one hour
- 125% load for four hours
NEMA
ALSO requires that there is a 50% load preceding and following the overload. So it's not a good idea to COUNT ON this overload capability unless you can control ALL aspects of the load.
Utilities have their own set of rules and design decisions, so they will often over-burden a pole pig transformer well beyond what we are allowed to do.