roberius

Member
Location
AIken SC
Can a wye generator run a delta system?
I know it doesn't and have proved it but, how do I explain it?
We got 480v coming in from the WYE generator to the DELTA system. The CT's smoked. 277v on the 480v lines.


Thanks
 
Last edited:
I see no reason why it could not. You just don't run or connect a neutral wire. All the load sees is a set of three wires being brought to it. The load cannot discern how those wires are connected to each other at the generation end.
 
What he said. A 480Y/277 will be 480V line to line. A 480 Delta will also be 480 line to line.
Now if your delta distribution system is corner grounded or ungrounded with an unrepaired ground fault you will have serious problems.
 
They connected the neutral from the generator to ground.
Definitely the problem. The generator output (in its entirety) should be grounded at only one point, as with any supply, and in this case, determined by the grounded phase.

You grounded one point (the neutral) from the generator and a different point (B phase) at the load, which created a direct B-to-N short and is why you overloaded the CTs.
 
B phase on the Delta system is grounded.
And if done properly should only be bonded at the service disconnecting means, amd run separate EGC's beyond that. This is exactly what you would do with wye supply anyway.


They connected the neutral from the generator to ground.

If you have three pole breakers (switching grounded conductor on each circuit simultaneously with ungrounded conductors) you can do the wye thing fairly easily as long as there are no B to ground bonds and you have separate grounding bus at the main gear. If you have two pole breakers or fuses connecting the wye generator gets more involved
 
Are you allowed to let the neutral float in the generator? If so, wouldn't this work just fine?

I guess you would have to have a ground detector of some sort?
to a certain extent I don't see why one couldn't leave it float and ground a phase. If you bring the neutral out in any way then it must be the grounded conductor.

When it comes to NEC requiring the neutral to be the grounded conductor - it applies when you actually have a neutral to ground. Simple 120/240 single phase secondary configured to be used for 240 only (maybe to supply European equipment?)- ground one end and do not use the center tap for anything - really not any different.
 
.

Since the service the generator is feeding has a grounded "B" phase, would you need to ground a phase at the transformer?

If you did, it would have to be "B" phase of course.
Where you ground depends if your transfer arrangement is set up as separately derived system or not. For non separately derived, you already have bonding at the service equipment, your "grounded conductor" should not have any fuses in it and should not have any switches or circuit breakers unless they also simultaneously open all conductors of the circuit - and you should have a separate EGC run from transfer equipment to generator frame, but no bonding to the "B" phase, that would introduce parallel paths for the grounded circuit conductor.
 
Last edited:
190611-0751 EDT

Whether something is a wye or delta has to do with wiring or configuration of the device.

Wye or delta alone says nothing about grounding. If you want to define how it is grounded, then you must add some qualifier to indicate means of grounding, if there is any grounding.

In many large industrial plants floating deltas are used. Where the lines (wiring) float relative to ground (earth) is determined by distributed capacitance and leakage of the distribution wiring and loads.

The words alone of wye or delta do not require or imply any grounding. Many, possibly most, electricians make some assumption of a particular way of grounding for a wye or delta. This can be a major mistake as indicated by this thread.

.
 
190611-0751 EDT

Whether something is a wye or delta has to do with wiring or configuration of the device.

Wye or delta alone says nothing about grounding. If you want to define how it is grounded, then you must add some qualifier to indicate means of grounding, if there is any grounding.

In many large industrial plants floating deltas are used. Where the lines (wiring) float relative to ground (earth) is determined by distributed capacitance and leakage of the distribution wiring and loads.

The words alone of wye or delta do not require or imply any grounding. Many, possibly most, electricians make some assumption of a particular way of grounding for a wye or delta. This can be a major mistake as indicated by this thread.

.

Correct. Where some get confused is NEC requires the neutral to be the point that is grounded. If you are not utilizing the neutral for any loads you don't necessarily have a neutral and can leave it as an internal point in the source and only bring out the three other leads for utilization, in that case to have a grounded system you must ground one of those three leads.

We do this all the time with delta systems made up of a bank of single phase transformers. Each one has a mid point, but we build a corner ground system by not tying into any of those mid point taps. Tie into one of them with a conductor for utilization purposes and it must become the grounded conductor per NEC and you end up with a high leg system.
 
Correct. Where some get confused is NEC requires the neutral to be the point that is grounded. If you are not utilizing the neutral for any loads you don't necessarily have a neutral and can leave it as an internal point in the source and only bring out the three other leads for utilization, in that case to have a grounded system you must ground one of those three leads.

We do this all the time with delta systems made up of a bank of single phase transformers. Each one has a mid point, but we build a corner ground system by not tying into any of those mid point taps. Tie into one of them with a conductor for utilization purposes and it must become the grounded conductor per NEC and you end up with a high leg system.

Can a Three-phase 480VAC generator be connected as a wye source to a delta-connected load?
 