You can still use MWBC in the '08, just have to use handle ties. Some people think that 2 pole, common trips is what's required, but you can just tie the handles.km5qd said:Home runs per 2005 9 circuits, 3 neutrals, 1 ground all #12 in 3/4" emt.
Home runs per 2008 9 circuits, 9 grounded conductors 1 ground all #10 in 1" emt.
Is this project at the college for dorms?