Gear this large is likely to be serviced/repaired at well below replacement cost.
Even if its 60 years old?
Gear this large is likely to be serviced/repaired at well below replacement cost.
Even if its 60 years old?
If you had the specs on the broken connector rod, how much do you think it would cost for the local machine shop to make one up for you?
cool pics but not sure I want parts made by a 3-D printer ! :happyno:
What is weird is I only see 3 primary stabs (poles) sticking out the top on each breaker!
Their should be 6 (3 line & 3 load)
Are these grounding trucks to ground the bus during maintenance??
A good point. Assuming you can get replacement parts of course.Gear this large is likely to be serviced/repaired at well below replacement cost.
I agree with ATSman....these are not breakers. They must be for grounding. I worked nuclear plants back in the late 70's and Magneblast 4160 breakers were what ran most of the MV motors. They had 6 stabs. DC connectors were for the elevator motors and coils. Control power was 125VDC on most. They connected when the breaker was rolled in. Jumper connectors were used to operate them outside of the enclosure for maintenance. There are breakers for sale on Ebay for less than $2000.
Rack out 4160 volt switch gear breakers made by GE. Few questions:
1) What does the current interrupting? (oil, SF6, air, ect)
2) What is the approximate age of these breakers? The gear they came out of is at least 40 years old.
3) How much would it cost to rebuild and refurbish these breakers- assuming its doable or economical?
4) Do they make new or after market replacements that will fit the gear- or is it better to just purchase new gear altogether?
Any additional info about these welcome.
1) Air, those are original GE Magneblasts
2) I would guess the 1950's
3) Very doable, I have 12 in my shop right now being remanufactured, price varies a lot depending on what parts need replacement (Those pole are probably bad) and if they want to do upgrades (There are 43 of them). Figure $8k to start
4)There are several roll in replacement options, I probably have a few hundred roll in VCB's from different OEM's plus we manufacture new replacements for these. Weak link of that gear is the cell bottles, that can be an expensive fix, but we do it all the time.
1) Air, those are original GE Magneblasts
2) I would guess the 1950's
3) Very doable, I have 12 in my shop right now being remanufactured, price varies a lot depending on what parts need replacement (Those pole are probably bad) and if they want to do upgrades (There are 43 of them). Figure $8k to start
4)There are several roll in replacement options, I probably have a few hundred roll in VCB's from different OEM's plus we manufacture new replacements for these. Weak link of that gear is the cell bottles, that can be an expensive fix, but we do it all the time.
If you had the specs on the broken connector rod, how much do you think it would cost for the local machine shop to make one up for you?
Much thanks!
How often do such breakers need testing or overhaul? I don't think these were touched for several decades beyond general maintenance.
Should be tested every few years (How often depends on environment and criticality) , overhaul every 10-20 years depending on # of operations, nuclear plants do overhauls every 8-10 years on these. Eventually the grease will dry out and only way to fix that is a complete overhaul.
The weak point on these is the poles, they were paper based back then and will absorb moisture, sometimes we can bake them out (I have a custom oven for these) but usually they have to be replaced with new ones that use modern insulating materials. But overall these are tanks, likely the most reliable breaker ever made, couple years ago I had the pleasure of meeting the engineer that designed these.
P.S. I looked at these on my phone last night but after a better look today I agree with ATS that these are grounding trucks.