copper chopper
Senior Member
- Location
- wisconsin
can i bring hdpe underground into a building and then transition to sch 80 pvc or rigid pipe to emerge up thru concrete floor and into a box..
353.12 Uses Not Permitted. HDPE conduit shall not be
used under the following conditions:
(1) Where exposed
(2) Within a building
(3) In any hazardous (classified) location, except as permit-
ted by other articles in this Code
(4) Where subject to ambient temperatures in excess of
50?C (122?F) unless listed otherwise
It cannot go within the building. To me that means it cannot physically enter the structure.
If the hdpe conduit contains service conductors:can i bring hdpe underground into a building and then transition to sch 80 pvc or rigid pipe to emerge up thru concrete floor and into a box..
230.6 Conductors Considered Outside the Building.
Conductors shall be considered outside of a building or
other structure under any of the following conditions:
(1) Where installed under not less than 50 mm (2 in.) of
concrete beneath a building or other structure
(2) Where installed within a building or other structure in a
raceway that is encased in concrete or brick not less
than 50 mm (2 in.) thick
(3) Where installed in any vault that meets the construction
requirements of Article 450, Part III
(4) Where installed in conduit and under not less than
450 mm (18 in.) of earth beneath a building or other
structure
(5) Where installed in overhead service masts on the outside
surface of the building traveling through the eave
of that building to meet the requirements of 230.24
As Rob points out, it is subject to what is considered within the building. My opinion differs from his... but its not either of our opinions which count. Suggest contacting the AHJ to get an official ruling prior to installation.this is for parking lot lights, also there is a reference to 300.5 an 300.50 in article 353 under uses permtted, does those articles mean its ok to use the original idea i posted???
under the slab is outside the building per the nec. Think service conductors to a main panel.
I have never quite understood why it is Ok to use smurf tubing, PVC or NM inside a building but not HDPE.
Possibly because of smoke producing characteristics? Not that you really want to be breathing combustion products of PVC either.
PVC is inherently fire retardant.I have never quite understood why it is Ok to use smurf tubing, PVC or NM inside a building but not HDPE.