Reducing wire size at OCPD. Correct me if im wrong....
Reducing wire size at OCPD. Correct me if im wrong....
I was always under the impression that if you increased your wire size to account for voltage drop, it has to be from ocpd to your load. Splicing a smaller conductor at the ocpd so it fits the lug properly to me seems like all your effort to increase the other 500' of conductor is totally defeted. What good does having a larger conductor do for you when you choke down the circuit at the start of it? Also you talk of a reducing lug of some kind but does Square D or any other manufactor approve this?
Reducing wire size at OCPD. Correct me if im wrong....
I was always under the impression that if you increased your wire size to account for voltage drop, it has to be from ocpd to your load. Splicing a smaller conductor at the ocpd so it fits the lug properly to me seems like all your effort to increase the other 500' of conductor is totally defeted. What good does having a larger conductor do for you when you choke down the circuit at the start of it? Also you talk of a reducing lug of some kind but does Square D or any other manufactor approve this?