big john
Senior Member
- Location
- Portland, ME
I would not fill the pipe with silicone. For one thing, I don't think it will stop the leak, in addition to making the raceway virtually useless in the future. I have also seen the damage that even a small amount of curing silicone will do to copper conductors and wouldn't want anything to do with putting an entire tube in a conduit.
I have used the Polywater product successfully in the past, but for me that would be a last resort because water is notoriously difficult to hold back permanently.
First choice would be find a mechanical solution to prevent the water from reaching the panel. Come in above grade, arrange it to drain, changeover to direct-burial cable, whatever.
I have used the Polywater product successfully in the past, but for me that would be a last resort because water is notoriously difficult to hold back permanently.
First choice would be find a mechanical solution to prevent the water from reaching the panel. Come in above grade, arrange it to drain, changeover to direct-burial cable, whatever.