Hi all,
The site got 208V, 1200A utility service and there's an existing 208/120V to 480V step-up transformer to feed some 480V machine. Also there's a 480V, 400A AC disconnect on high voltage side of the transformer. We want to avoid 208V inverters as much as possible in this project so can we do the interconnection on the 480V disconnect of the transformer?
The transformer nameplate is below and our intended inverter is 480V, 120kW.

	
		
			
		
		
	
				
			The site got 208V, 1200A utility service and there's an existing 208/120V to 480V step-up transformer to feed some 480V machine. Also there's a 480V, 400A AC disconnect on high voltage side of the transformer. We want to avoid 208V inverters as much as possible in this project so can we do the interconnection on the 480V disconnect of the transformer?
The transformer nameplate is below and our intended inverter is 480V, 120kW.

 
				


 
 
		 .    This Just recently came up in another thread, and I was surprised that the ground detector requirement came in in the 90s, IIRC.  Keep in mind, also, some states like New York are typically 8 years behind on their code adoption.  Perhaps that transformer has the date of manufacture on it which would help pinpoint whether the installation was compliant or not at the time.
.    This Just recently came up in another thread, and I was surprised that the ground detector requirement came in in the 90s, IIRC.  Keep in mind, also, some states like New York are typically 8 years behind on their code adoption.  Perhaps that transformer has the date of manufacture on it which would help pinpoint whether the installation was compliant or not at the time.