I think the only concern with art 312 would be the amount of wiring space the added device may take up, typical in line fuse holder however probably is not going to be a problem.
Then there is 240.24(A) Accessibility: "Overcurrent devices shall be readily accessible and...:
This rule doesn't apply to supplemental overcurrent devices.