broadgage
Senior Member
- Location
- London, England
It should be fine.
The nominal or declared voltage in the UK is 230 volts, and the maximum permitted is 253 volts (230 +10%)
Therefore the measured on load voltage of 250 volts is within the UK permitted tolerance.
If the motor is an induction motor, and was designed for 50 cycles, then at 60 cycles it will run faster, and develope more horsepower. This is unlikely to lead to overheating since the internal cooling fan will also run faster.
If the motor is a brush type, then the increased frequency is of almost no importance and the motor will be fine.
It might be prudent to re-check the on load voltage at different times of day, in case it rises above 253 volts at times of low load/increased voltage from your utility.