I am working on a large office building and there will be PV arrays mounted on a structure in the parking lot. No arrays will be mounted on the building. The building will have a dedicated pad-mounted utility transformer. I also have a fire pump that I need to run a dedicated service to as well. For a grid-tie, net metering system, can I run the PV service directly to the secondary side of the transformer? I've attached a sketch of what I'm thinking. This will make the install a lot cleaner on my end.
Also, I haven't run into this situation where I possibly could have too many conductors for the secondary side. At what point would I need a secondary bus enclosure?
Thank you.
  • Electric Service Notes.pdf
You would have to ask the utility if they allow it. The utility might need to meter your solar with a net meter. Maybe they can true up a performance meter instead. Like totalize the solar as subtracting from the normal load meter. But, that is up to them.
Thank you.
If the POCO meters the service at the transformer, and if you can land your PV conductors on the load side of their metering CTs, and if the POCO allows it, then sure. That's a lot of ifs, though.
I’ll finish the design and get everything in the hands of the POCO. I’ll come back with an update.
If the meter and CT can are on the wall of the building and away from the transformer you won't be able to connect at the transformer.
Not sure if you're diagram was supposed to have some connecting lines but I see an ATS and a grid-tied PV system would need to be interconnected on the line side of the ATS.
There really should be no reason you can't come off the service to a separate PV disconnect, if this is being built new. Just call it an additional service disconnect.