Can I swap a 55A breaker with a 60A breaker?

Status
Not open for further replies.
THW AL gives some idea of the probable age of the install but, curious, was 55 amp ever a "standard size" ?
Seemingly someone went out of their way to use such.
I kind of doubt it was ever a standard size. I could see some sort of OEM version being produced for some specific equipment that someone happened to have ready access to though.
 
THW AL gives some idea of the probable age of the install but, curious, was 55 amp ever a "standard size" ?
Seemingly someone went out of their way to use such.
I think at one time you could get residential circuit breakers in 5 Amp increments all the way up to 70 or maybe 75 A.
 
THW AL gives some idea of the probable age of the install but, curious, was 55 amp ever a "standard size" ?
Seemingly someone went out of their way to use such.
6 copper @ 60C has ampacity of 55, so possibly could have been for that reason if it was common or even a standard size?
 
hmmm how so? am I missing something?
#4 THW AL has an ampacity of 65 amps. Provided you have 75° terminations and no derating (ambient, fill, etc) the 240.4 would allowa 70 amp breaker (assuming a load of no more than 65 amps)
 