A 120/240 volt single phase, 3wire feeder supplies 150 general purpose recepticals in an office building with 3200 square feet. When sizing this feeder, what will be the minimum calculated amperage load to be used?
Answer: 77 amperes.

The reference i was given is table 220.44 and 220.14(k). Can anyone please help explain this? I have calculated it many different ways and can not get 77 amperes. Sorry if I didn’t post this right. I am new to the forum.
 
3200sqft x 3va/sqft=9600va

9600va divided by 120V= 80 amperes.
Table 220.44 demand factor says first 10kva at 100%

But 220.14 (h) and (I) says to use 180va for each outlet.
180va x 150=27000va
27000 divided by 120v =225 amperes.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
3200sqft x 3va/sqft=9600va

9600va divided by 120V= 80 amperes.
Table 220.44 demand factor says first 10kva at 100%

But 220.14 (h) and (I) says to use 180va for each outlet.
180va x 150=27000va
27000 divided by 120v =225 amperes.


Try using 240V for starters.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I think the key may be they are asking you to calculate the receptacle load only.
220.4(K) + 220.44 gives you the 77 amps I believe.
 

topgone

Senior Member
3200sqft x 3va/sqft=9600va

9600va divided by 120V= 80 amperes.
Table 220.44 demand factor says first 10kva at 100%

But 220.14 (h) and (I) says to use 180va for each outlet.
180va x 150=27000va
27000 divided by 120v =225 amperes.
Why do you use 3 VA/sq, ft.? Receptacles will be given 180 VA/strap.
 

Ingenieur

Senior Member
Location
Earth
Got it ! Thanks for the help

friendly word of advice since you are a newby
when a member gives advice (eg use 240)
think about it before dismissing it out of hand
look who's giving it
post count
he's a moderator for one, meaning they trust him technically
two, look at their profile
he's an EE and a PE likely with decades of experience
good chance he knows what he is talking about if he took time to answer/help