This article never made sense to me, and I think it should be dropped.  I don?t believe that the physics of the situation supports the requirement.  
 
Consider the following example (NOTE:  This is a discussion of physics, not code, so please don?t cite 250.122 back at me):
?         20 amp breaker, #12 wire, ?fairly long run,? total voltage drop at 3.2%.
?         Nothing requires me to upsize the conductors (i.e., VD is not a code requirement).
?         I infer that there is a low enough impedance in the #12 conductors, including the #12 EGC, to result in a high enough fault current to trip the breaker, should there be a fault at the end of the run.
?         Let me emphasize:  This is a safe installation, because I have confidence that the OCPD would trip, on a fault.  The fault current is high enough already!
?         Now I choose to replace the phase conductors with #10.  I have not yet biggie-sized the EGC.
?         That just caused the overall circuit impedance, in the event of a fault, to be lower than it was before.
?         Therefore, the fault current will be higher than it was before.
?         Therefore, the OCPD will trip even faster.
?         Now, tell me, from a physics point of view, why I need to increase the fault current even more, by using a #10 EGC?