hockeyoligist2
Senior Member
- Location
- close to greenville sc
I am being asked to explain why we needed a more expensive motor for a piece of equipment.
Two identical machines, fully enclosed motors, no fan, 1/2 HP, FLA 1 Amp, SF 115, 480 V. A few weeks after they were installed by the contractor an operator burned his hand (blister) on one of the motors when he accidentally touched it. I checked the amps on both motors and they were pulling 1.30 amps.
I talked with engineering and asked them to have the manufacturer check them out. It was obviously under powered. Manufacturer said it is normal and the amps will drop after break in period. Engineering let it slide. The amps never dropped. A few weeks after the warranty ran out one motor finally let the smoke out. I wasn't there at the time and they replaced it with a Baldor, 1/2 HP, SF 1, it lasted 6 months.
When the Baldor let the smoke out, I bought a 3/4 HP, with a SF of 115, and replaced it. It was about $100 more than the first replacement motor. It is pulling 1 amp, barely warm to the touch.
I just got an E-mail from purchasing (non-electricians) wanting an explanation on my decision to spend the extra money. I am authorized to make that decision, however, I have to explain my decision to them. They are also asking why the original motor on the other machine is still running and the Baldor conked out so quick.
I've Googled for something to print out for them with no success. Trying to explain the difference in SF and an under powered motor to someone that doesn't know anything about motors (or anything electrical) is hard. All they know is $'s!
Two identical machines, fully enclosed motors, no fan, 1/2 HP, FLA 1 Amp, SF 115, 480 V. A few weeks after they were installed by the contractor an operator burned his hand (blister) on one of the motors when he accidentally touched it. I checked the amps on both motors and they were pulling 1.30 amps.
I talked with engineering and asked them to have the manufacturer check them out. It was obviously under powered. Manufacturer said it is normal and the amps will drop after break in period. Engineering let it slide. The amps never dropped. A few weeks after the warranty ran out one motor finally let the smoke out. I wasn't there at the time and they replaced it with a Baldor, 1/2 HP, SF 1, it lasted 6 months.
When the Baldor let the smoke out, I bought a 3/4 HP, with a SF of 115, and replaced it. It was about $100 more than the first replacement motor. It is pulling 1 amp, barely warm to the touch.
I just got an E-mail from purchasing (non-electricians) wanting an explanation on my decision to spend the extra money. I am authorized to make that decision, however, I have to explain my decision to them. They are also asking why the original motor on the other machine is still running and the Baldor conked out so quick.
I've Googled for something to print out for them with no success. Trying to explain the difference in SF and an under powered motor to someone that doesn't know anything about motors (or anything electrical) is hard. All they know is $'s!