Does surge protective device really a ground to shunt the current or can it resist them by its own (when say connecting line to line (or directly put between the black and red wire in the 240v in US power system).
See technical paper at:
http://www.surgesuppression.com/ima...licationofSurgeSuppressionRevDate10202005.pdf
"Power was applied to Phase A and B and thermometer was used to measure the temperature of the MOV when surge was introduced (details in the paper above). Based on the much higher temperature rise in the discrete line-to-line MOV, the discrete line-to-line MOV absorbs a much larger portion of the surge current and energy than the combination of the two line-to-neutral paths.
See the following image:
Someone told me varistors don't really need ground to shunt the current. He said that there was no minimum input voltage anywhere. And the physics of an MOV do not show any minimum either.
He said that the Zinc Oxide grains were close enough to each other that they are in light electrical contact, with very little current able to flow between them; probably due to the oxide layer on their surfaces. Higher voltages are able to break down this oxide layer and allow more current to flow. That's how they suppress surges, by conducting the higher voltages, usually to ground, but blocking current when only the lower normal operating voltage is present. But without ground, then the varistors (MOVs) just heat up. That's how it can be connected line to line without ground.
So Surge Protective Devices can be connected directly between line to line right? and if there are surges, it just heats up (and degrades a bit). But compared to having access to ground. How good can it still dissipate the energy by heating up (without any access to ground)?
What do you think?
See technical paper at:
http://www.surgesuppression.com/ima...licationofSurgeSuppressionRevDate10202005.pdf
"Power was applied to Phase A and B and thermometer was used to measure the temperature of the MOV when surge was introduced (details in the paper above). Based on the much higher temperature rise in the discrete line-to-line MOV, the discrete line-to-line MOV absorbs a much larger portion of the surge current and energy than the combination of the two line-to-neutral paths.
See the following image:
Someone told me varistors don't really need ground to shunt the current. He said that there was no minimum input voltage anywhere. And the physics of an MOV do not show any minimum either.
He said that the Zinc Oxide grains were close enough to each other that they are in light electrical contact, with very little current able to flow between them; probably due to the oxide layer on their surfaces. Higher voltages are able to break down this oxide layer and allow more current to flow. That's how they suppress surges, by conducting the higher voltages, usually to ground, but blocking current when only the lower normal operating voltage is present. But without ground, then the varistors (MOVs) just heat up. That's how it can be connected line to line without ground.
So Surge Protective Devices can be connected directly between line to line right? and if there are surges, it just heats up (and degrades a bit). But compared to having access to ground. How good can it still dissipate the energy by heating up (without any access to ground)?
What do you think?